Questions answered
Wire, fuse and inverter questions, answered
Wrong wire and fuse sizes are where camper fires start. These answers come from Blue Sea Systems' ABYC-based guides and Victron's wiring book.
Updated October 24, 2026. Every answer lists the sources we read it from. Prices are the makers' own, from the day we last checked.
Disclosure: We may earn a commission if you buy through these links. It never changes what we recommend or what the tools calculate. How we make money.
What size fuse do I need between the battery and the inverter?
Short answer
Size it from the inverter's input current. A 2,000 W inverter on 12 V draws about 196 A at full load (2,000 W / 12 V / 85% efficiency), and Blue Sea's minimum fuse is 125% of the current, so a 250 A fuse. The cable must be rated for at least the fuse, and if the inverter maker specifies a fuse, follow the manual.
| Inverter | Current at full load | Fuse | Cable |
|---|---|---|---|
| 1,000 W, 12 V | 98 A | 125 A | 2 AWG |
| 2,000 W, 12 V | 196 A | 250 A | 3/0 AWG |
| 2,000 W, 24 V | 98 A | 125 A | 2 AWG |
The 85% efficiency is the figure Redodo uses in its own inverter manual. Blue Sea's rule: the fuse protects the wire, so it may never be larger than the wire's rating; if the maker's fuse is too big for your wire, use bigger wire.
For your own rig: Full wire gauge and fuse chart
Renogy Class T Fuse with Holder
Class T fuse and holder for the battery positive. $18.99 for the 250 A size, $26.99 for 150 A or 350 A the day we checked.
What size wire from the battery to a 2000 W inverter?
Short answer
On 12 V, 3/0 AWG for a run of 8 feet or less, with a 250 A fuse, using ABYC's rating for bundled cable. On 24 V the current halves and 2 AWG does the job. Keep the inverter close to the battery: Redodo's manual says to place them as close as possible to cut voltage loss.
Victron's wiring book explains why voltage matters: for the same load, doubling the system voltage halves the current, and the cable voltage drop falls with it.
The negative cable carries the same current back, so it gets the same size.
For your own rig: Cable sizes for other lengths
Redodo 2000W Pure Sine Inverter (12V)
2,000 W continuous, 4,000 W surge, 90% efficiency per Redodo. Runs a microwave or a coffee maker.
$205.99$359.99
See at Redodo (opens in a new tab)What gauge wire do I need for 30 amps, or any 12 V load?
Short answer
It depends on the round-trip length and how much voltage drop the circuit can take. Blue Sea's method, from ABYC E-11: measure from the battery to the load and back, allow 3% drop for critical circuits such as electronics and main feeders or 10% for general lighting and appliances, then read the gauge off the table. Our wire chart does that for 12 V and 24 V.
Blue Sea's own example: an 80 A windlass 25 feet from the battery is a 50-foot circuit, non-critical, and needs 4 AWG.
ABYC-grade marine wire is stranded, tin-plated copper, and Blue Sea's chart assumes 105°C insulation; a lower rating carries less current.
For your own rig: 12 V and 24 V wire gauge chart · Gauge and fuse on every run (wiring tool)
Do I need a Class T fuse for a lithium battery?
Short answer
You need at least one fuse that can safely break a lithium short circuit, and Victron calls the Class T well suited to that job. Victron makes it a mandatory safety requirement because lithium batteries can deliver very high short-circuit currents. Class T fuses are rated to interrupt 20,000 A or more, against 6,000 A for a Blue Sea ANL and 1,000 to 2,500 A for MEGA fuses.
Victron's rule: the fuse's interrupt rating must be at least the battery bank's maximum short-circuit current. A fuse with too low a rating can fail catastrophically instead of opening.
The Renogy Class T Fuse with Holder was $18.99 for the 250 A size the day we checked.
Renogy Class T Fuse with Holder
Class T fuse and holder for the battery positive. $18.99 for the 250 A size, $26.99 for 150 A or 350 A the day we checked.
Should I ground my van's electrical system to the chassis?
Short answer
Use one ground point, close to the battery. Victron's guidance is to make the battery ground the most reliable connection, with ground cable thick enough to carry a fault current at least equal to the DC fuse rating, and to ground the inverter's chassis. Victron also says not to ground the positive or negative of the solar array, because on its controllers the PV negative is not isolated from the battery negative; the panel frames may be grounded.
Victron also notes that on its inverters of 1,600 VA and up, the AC neutral is connected to the chassis, so grounding the chassis also grounds the AC neutral. AC grounding and shore power bonding belong to a qualified electrician.
Should I build a 12 V or 24 V system?
Short answer
It mostly comes down to inverter size. Victron's preferred limits are up to 3,000 VA on 12 V and up to 5,000 VA on 24 V, because a higher system voltage means lower current and thinner cable. If some loads or chargers only work on 12 V, Victron suggests DC-DC converters rather than keeping the whole system at 12 V.
Victron's example: a 2,400 W load draws 100 A at 24 V, and the cable voltage drop in its example falls from 5% at 12 V to 1.3% at 24 V.
Price check the day we checked: the Redodo 24V 100Ah was $469.99; two Redodo 12V 100Ah Group 31 Bluetooth batteries were $521.98.
For your own rig: The planner picks 12 V or 24 V for your loads
Redodo 24V 100Ah
2,560 Wh at 24 V with a 100 A BMS: a 2,000 W inverter draws about 93 A at 24 V, inside that limit.
$469.99$759.99
See at Redodo (opens in a new tab)How big an inverter do I need?
Short answer
Add up the watts of everything that will run at the same time and pick an inverter whose continuous rating is above that. Redodo's manual says the load must stay under the inverter's continuous power and warns that some devices surge at start-up; its 2,000 W model is rated for a 4,000 W peak. Don't oversize: bigger inverters need much thicker cable.
Check the label on each appliance for its input watts, and switch the inverter on before the loads, as Redodo advises, so a start-up surge doesn't trip it.
Two sizes we list: the Renogy Pro 1000W Pure Sine Inverter (12V) ($222.99) and the Redodo 2000W Pure Sine Inverter (12V) ($205.99), prices from the day we checked.
For your own rig: Inverter sized from your list of AC loads (planner)
Renogy Pro 1000W Pure Sine Inverter (12V)
1,000 W is plenty for laptops, a CPAP, camera batteries and a small TV.
Redodo 2000W Pure Sine Inverter (12V)
2,000 W continuous, 4,000 W surge, 90% efficiency per Redodo. Runs a microwave or a coffee maker.
$205.99$359.99
See at Redodo (opens in a new tab)Safety first
Fuse every positive wire as close to the battery or bus bar as you can, and use the wire and fuse sizes from a standard table, not a guess. Boats should follow ABYC E-11; anything that touches 120/240 V AC should follow the NEC. Have a qualified installer check any 120/240 V AC or shore power work.
Run the power planner
Battery, solar, charger, inverter, every wire and fuse, and a priced parts list.
Draw your wiring
Drag parts onto a diagram and get gauge and fuse labels on every run.
More questions answered
Keep going
Van electrical basics
The six parts every camper system has, how they connect, and a diagram to download.
Wire gauge and fuse chart
12 V and 24 V wire sizes and fuses by amps and run length, from the ABYC tables.
Power station vs built-in
When a Bluetti box beats a wired system, and when it costs you more.